So according to the video the delta configuration (or was it the star) has a huge starting amperage requirement. Is this a problem for you Emiliano?
Wye/Star - Delta motor starting is used for several reasons and solves a couple of problems that various applications create. For a starting a heavy load that takes time to come up to speed, a Wye/Star winding is used to reduce the voltage drop and handle high currents on the electrical system. Once the motor and load comes up to speed the starter switches the motor over to the Delta windings which is the more common mode used for running 3 phase motors. This method requires 6 leads going out to the motor and a starter with several contactors and a timer or load sensing circuit that switches the contactors between the Wye/Star configuration and the Delta configuration.
One of the most common applications is a centrifuge that takes time to come up to speed and draws high currents during the start up, if high currents are allowed to take place on your electrical system you end up with voltage drops affecting other equipment on the same electrical system. The Wye/Star start winding method reduces the voltage drop issue.