Steve W.,
Tsk, tsk, tsk. Bad boy, bad boy. 120 VAC outlets are not connected in series, They are connected in parallel. Don't confuse daisy chaining with series or parallel. It has nothing to do with either. There is not any particular reason that you could not have more than one receptacle on a 240 VAC branch circuit except that you normally run a 240 VAC circuit for a specific purpose whereas 120 VAC receptacles are typically general purpose.
Leslie,
For the Jet mini lathe, the answer is NO. You normally don't find dual voltage motors until you get up around 1 HP. These days, motors on woodworking machines are more likely to be single voltage units because of slightly lower cost. Look at the motor's nameplate -- it will answer your question. If it can be operated on either 120 or 240, it requires opening up the terminal box on the motor and switching some jumpers or leads around.
Mark and Gary7,
The 1.5 HP version of the Jet 1642 can only run on 120 VAC. The motor operates on 230 VAC, but the inverter uses 120 VAC -- converts it to approximately 325 VDC and then it is converted to a synthesized 230 volt sine wave at the desired frequency (at low frequencies, it is less than 230 volts to prevent magnetic saturation of the iron. The only way to change this is to change the inverter or find out if there is another AC to DC board for that particular inverter that is designed for 240 VAC input.
Bill